A 10000 ft^2 Auditorium with 30 ft celings requires 5 air changes per hour, what is the required CFM? Since we are posting engineering questions..lol
25,000 CFM

Auditorium = 300,000 cf divided by 60 minutes = 5000 CFM for one air change x 5 = 25k CFM

 
A 10000 ft^2 Auditorium with 30 ft celings requires 5 air changes per hour, what is the required CFM? Since we are posting engineering questions..lol
25,000 CFM
Auditorium = 300,000 cf divided by 60 minutes = 5000 CFM for one air change x 5 = 25k CFM
Correct and in less than 6 minutes, you sir diserve a :bananalama:

 
A 10000 ft^2 Auditorium with 30 ft celings requires 5 air changes per hour, what is the required CFM? Since we are posting engineering questions..lol
25,000 CFM
Auditorium = 300,000 cf divided by 60 minutes = 5000 CFM for one air change x 5 = 25k CFM
Correct and in less than 6 minutes, you sir diserve a :bananalama: