This problem is fuse sizing to protect conductors against short circuit and ground faults with a motor in the circuit.
The way the answer is given in the book is not to consider the ampacity of the conductors when a motor is in the circuit since the conductors are protected against overload by the motor-overload device and to use table 430.52 for fuse selection with the only concern for short circuit and ground faults.
Now if I change this problem a little by eliminating the motor from the circuit, I now must consider the ampacity of the conductors for fuse selection.
So my thought process for fuse selection criteria is if a motor is in the circuit be concerned with short circuit and ground faults. If there is no motor in the circuit than be concerned with the ampacity of the conductors. Is that correct?
The way the answer is given in the book is not to consider the ampacity of the conductors when a motor is in the circuit since the conductors are protected against overload by the motor-overload device and to use table 430.52 for fuse selection with the only concern for short circuit and ground faults.
Now if I change this problem a little by eliminating the motor from the circuit, I now must consider the ampacity of the conductors for fuse selection.
So my thought process for fuse selection criteria is if a motor is in the circuit be concerned with short circuit and ground faults. If there is no motor in the circuit than be concerned with the ampacity of the conductors. Is that correct?