I have few more questions about neutral current and harmonics:
1. For a balanced three phase system 3rd harmonics will be three in the system (and hence flow through neutral) only if any non-linear load is there in the system?
2. Is there third harmonics are present only in 3-phase, 4 wire Wye system not in delta system?
3. For a 3-phase to ground fault we say, Ia+Ib+Ic=0 and In=0 too.
Is it correct to say that during 3-phase fault current in the neutral is zero ?
4. Also the multiple of 3 of 3rd harmonics are zero sequence harmonics. So is it in a 3-phase balanced system the other positive and negative sequence harmonics cancel out each other??