Hi, guys just joined the form! I'm taking the test next week, and one thing I'm a little iffy on is when to use the total heat equation vs. sensible. Most the time, I can determine from the problem which one to use, but for example problem #42 on the engineer pro guides practice test is giving me a little trouble.
Problem: The AHU serving the classroom has a supply temperature of 55F and the space is to be maintained at 75db/50%RH, what CFM is required?
Given: 25 people @ 250btu/person (sensible) & 200btu/person (latent)
Lighting = 4,000 btus; Computers =8,000 btus; Walls, Roofs, Windows = 22,000 btus; Ventilation = 7,500 btus (sensible) 7,500 (latent)
Answer Choices: (A) 2,210 CFM; (B) 2,675 CFM; (C) 2,790 CFM; (D) 3,865 CFM..............Correct Answer (A)
My Solution: Since there is a latent load from ventilation and people I assumed I would have to use Q(Total) = CFM*delta(H)*4.5 Btuh...so after totaling up the sensible & latent loads, getting the enthalpy values of the psych chart, and solving for CFM I got an answer of (B) 2,675 CFM...which is wrong. The solution to the problem only accounts for the sensible heat and used Q(sensible) =1.08*CFM*delta(T) to get answer of (A)2,210 CFM.
What key concept am I missing here? My though process so far has been if your sizing and kind of equipment/or coil you need to account for both sensible & latent loads. The only time you can use sensible only, is when there is no latent loads present?
Any help will be greatly appreciated! Thanks.
Problem: The AHU serving the classroom has a supply temperature of 55F and the space is to be maintained at 75db/50%RH, what CFM is required?
Given: 25 people @ 250btu/person (sensible) & 200btu/person (latent)
Lighting = 4,000 btus; Computers =8,000 btus; Walls, Roofs, Windows = 22,000 btus; Ventilation = 7,500 btus (sensible) 7,500 (latent)
Answer Choices: (A) 2,210 CFM; (B) 2,675 CFM; (C) 2,790 CFM; (D) 3,865 CFM..............Correct Answer (A)
My Solution: Since there is a latent load from ventilation and people I assumed I would have to use Q(Total) = CFM*delta(H)*4.5 Btuh...so after totaling up the sensible & latent loads, getting the enthalpy values of the psych chart, and solving for CFM I got an answer of (B) 2,675 CFM...which is wrong. The solution to the problem only accounts for the sensible heat and used Q(sensible) =1.08*CFM*delta(T) to get answer of (A)2,210 CFM.
What key concept am I missing here? My though process so far has been if your sizing and kind of equipment/or coil you need to account for both sensible & latent loads. The only time you can use sensible only, is when there is no latent loads present?
Any help will be greatly appreciated! Thanks.