NEC Table 400.5(A)(1) for Flexible Cords and Flexible Cables: Cram for Exam Vol. 4 Question 52

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

akyip

Well-known member
Joined
Feb 7, 2020
Messages
422
Reaction score
203
Hey guys,

I'm working on code questions from Cram for Exam Vol. 4. Question 52 is about allowable ampacity for type ETT flexible cord:

"A #8 AWG, two-conductor flexible cord type ETT is to be used in a construction atmosphere. What is the allowable ampacity of the cord?"

The solution says that the answer is choice C = 35 A based on Table 400.5(A)(1), but upon looking more carefully at this table, shouldn't it be 40 A instead?

The 35 A for type ETT #8 AWG flexible cord is listed under Column A, which per the notes below the table apply to 3-conductor cords.

On the other hand, Column B for ETT #8 AWG flexible cord has 40 A under Column B, which per the notes below the table apply to 2-conductor cords. And the given flexible cord in the problem statement is 2-conductor.

See the attached photos for reference. So, shouldn't the correct answer be Choice D = 40 A instead? Or am I missing something here?

Cram for Exam Vol 4 Problem 52.jpg

Cram for Exam Vol 4 Solution 52.jpg

NEC Table 400.5(A)(1).jpg

 

Latest posts

Back
Top