What is the internal generated phase voltage in a 3 phase Synchronous generator. Given base values 250 KV, 100 MVA and Xd= 1.1 pu, steady state current =.97 pu
Don 3.0 I was trying to do it like that - E= 1+j 1.1 X 0.97; that gives you E= 1.46 pu ; the base phase voltage is 250/ sqrt3= 144 kV so the answer should be E=1.46 X 144=211 kV. But CI gives answer as 268KV. Am I wrong some where.For a sync. generator E = V + X*I where E is the internal generated voltage, V is the terminal voltage per phase, X is the sync. reactance, and I is the output phase armature current of the generator. Key things given to you that you need to catch right away and understand: "phase voltage", "generator", "base value", and per unit values. These determine how to approach the problem.
I have the same problem with this CI Exam 3 Problem 34. What is the clue that the generator has been short circuited? Is it because the current is called "steady state?"I got it now. The steady state condition given at I=.97 pu is a condition of fault and not a condition of a healthy Generator. CI is right it is E=Id *Xd and not V+IX.
Cos90, the question C-3(34) does not mention explicitly about short ckt. but yes as you say transient and steady state terms are used for fault conditions. How ever steady state condition can also a healthy condition but I think it is less frequently used. More confusing here was .97pu of current. It is near rated current and so it looks more like a healthy condition but I was happy to get the answer by multiplying something and I expressed it, specially in absence of contribution from anyone else on the forum.I have the same problem with this CI Exam 3 Problem 34. What is the clue that the generator has been short circuited? Is it because the current is called "steady state?"
Yes Eg is line to neutral Voltage and in the question also, it is asking phase voltage. Now the figures 250KV and 100MVA which are called rated values for the generator must be meant for 3phase as nothing otherwise is mentioned there. If that be the case the answer should be 154 KV and not 268KV.I think the convention for these equivalent circuit of an AC generator problems is that Eg is the line to neutral voltage of one terminal.
Please see this image from Elements of Power System Analysis by Stevenson
I think CI is right for this problem as long as you agree the generator terminals are shorted.
I find that these types of problems (equivalent generator and motor circuits) are always MUCH easier when we draw the diagram out.
This problem is essentially asking:
"what is the internal generated (stator) voltage (per phase) that would result in a stator current of 0.97pu if the stator reactance (per phase) is j1.1pu"
Then, they give you the base value of the voltage to multply your per unit answer with to get the actual value in volts.
Like this:
View attachment 9856
Hi
Thanks for the input. Will you take 250 KV base voltage as Line to line or it is Line to neutral? I thought base values are 3 phase values and the question is asking Generated Voltage in Phase to Neutral values. Will your answer not be 268/sqrt3=154kV?????
Make sense?
The stator terminals are not necessarily shorted.
Motor and generator equivalent circuits can be really difficult at first, but you'll find they are quite easy.
If you'd like more practice, we have a tremendous amount of worked out motor and generator equivalent circuits just like this one available inside our free electrical power review course
Electrical PE Review - Free Electrical Power PE Exam Review Course
Hi @rg1
It is easy to over complicate the per unit system but it helps to remember that Base values are just scalar multipliers.- I do not have any confusion in pu system
Three phase ratings of a machine are commonly used as base values. So the 250 KV given here is Line to Line Voltage
Since they gave you the three phase ratings in the question, without telling you the specific base value, AND gave you the answers in volts instead of pu, you have to work with what you've got and assume. My doubt is not in pu but whether the answer 268 KV is Line Voltage or Phase Voltage and did the question ask line Voltage or Phase Voltage? I suppose the Phase to Neutral Voltage in this case, as asked by the Question is 154 KV and options does not contain that option.
Making the correct assumptions comes with practice but is pretty straight forward after awhile. The pu value of answer is 1.067pu. I am with you till here. Taking it ahead I have to multiply it with Base value. Now base value of line voltage is given as 250KV, then 1-phase base value will be 144KV and answer will be 154KV. I am quite confident that I am right, untill I come to know that I am really missing something trivial.
Correct.So the 250 KV given here is Line to Line Voltage
So the 250kV is assumed to be the line to line voltage, and the 100MVA is assumed to be the total three phase apparent power it will deliver to the three phase system."What is the internal generated phase voltage in a 3 phase Synchronous generator. Given base values 250 KV, 100 MVA and Xd= 1.1 pu, steady state current =.97 pu"
My doubt is not in pu but whether the answer 268 KV is Line Voltage or Phase Voltage and did the question ask line Voltage or Phase Voltage? I suppose the Phase to Neutral Voltage in this case, as asked by the Question is 154 KV and options does not contain that option.
1
The solution of 268kV is the internal generated phase voltage, which is a per phase value.
This is usually shown as Eo or Vo on generator single phase equivalent circuits.
If you've ever seen one of these machines in person, it's the induced stator voltage in each phase produced from the excited, spinning rotor.
The question also gives you a clue: "What is the internal generated phase voltage"
Quote
The pu value of answer is 1.067pu. I am with you till here. Taking it ahead I have to multiply it with Base value. Now base value of line voltage is given as 250KV, then 1-phase base value will be 144KV and answer will be 154KV. I am quite confident that I am right, untill I come to know that I am really missing something trivial.
I think rg1 is correct. There is an identical question in CI that solves it by dividing the base voltage by sqrt 3. I will point out the discrepant questions when I get home.
Correct.
For any type of three phase or machine, the ratings and base values can almost always be assumed to be the three phase values unless explicitly stated otherwise.
For example, if you are sizing a three phase transformer, then you are most concerned with the total three phase power it can deliver - because it is going in a three phase system, and the three phase line to line voltage rating - because it is going to be connected across all three phases.
In this case, it is a three phase generator:
So the 250kV is assumed to be the line to line voltage, and the 100MVA is assumed to be the total three phase apparent power it will deliver to the three phase system.--
The 1.1pu Xd is assumed to be a single phase, or per phase reactance used in the single phase equivalent circuit since impedance is always dealt with on a per phase basis.
The Steady State Current of 0.97pu is assumed to be the stator current, as a result of the internally generated voltage (what the question is asking for) and the per phase reactance, Xd.
The solution of 268kV is the internal generated phase voltage, which is a per phase value.
This is usually shown as Eo or Vo on generator single phase equivalent circuits.
If you've ever seen one of these machines in person, it's the induced stator voltage in each phase produced from the excited, spinning rotor.
The question also gives you a clue: "What is the internal generated phase voltage"
I understand your confusion. Sometimes either the line voltage or phase voltage will be selected as the base. However, if the problem points it out directly, it is best to use the given the base value at face value:
"Given base values 250 KV"
Hope this helps. It does not help sir. It creates more confusion. I am clear. The issue here is only of convention and even after agreeing that 250kV is L-L voltage we are getting different answers.??? The student in me is not accepting your logic.
I'd be happy to discuss it further with you.It does not help sir. It creates more confusion. I am clear. The issue here is only of convention and even after agreeing that 250kV is L-L voltage we are getting different answers.??? The student in me is not accepting your logic.
Lol I am not confused, you are!!!. Anyways.I'd be happy to discuss it further with you.
Can you explain where you are confused?