Hello,
In the question below we are after the 3Phase fault current on the secondary of a 12.47/0.480 kV XFMR.
Now in addition to the XFMR parameters we are told the "Fault Duty" on of the 12.47kV side of the system.
My interpretation is that this represents the equivalent MVAsc of the system above the XFMR.
Based on this info I did the following:
Isc above the XFMR is Isc_12.47= MVAsc/ (12,470 * sqrt (3)) =1851.965 amps
Therefore Z_12.47kV= V/Isc= 12470/1851.965=6.73 ohms
Since the XFMR imp is already in pu i decided to convert Z_1247kV to pu as shown below:
Z_base= (0.480^2)/(10^6)
Z_12.47kV ref to secondary= Z_12.47kV/ (12.47/0.480)^2=0.009 ohms
Z_12.47kV_pu= Z_12.47kV ref to secondary/Z_base=0.0433 pu
When i looked at the solution what i saw is that the pu value NCESS gets is 0.025 pu
Does anyone see where i went wrong with my pu conversion?
In the question below we are after the 3Phase fault current on the secondary of a 12.47/0.480 kV XFMR.
Now in addition to the XFMR parameters we are told the "Fault Duty" on of the 12.47kV side of the system.
My interpretation is that this represents the equivalent MVAsc of the system above the XFMR.
Based on this info I did the following:
Isc above the XFMR is Isc_12.47= MVAsc/ (12,470 * sqrt (3)) =1851.965 amps
Therefore Z_12.47kV= V/Isc= 12470/1851.965=6.73 ohms
Since the XFMR imp is already in pu i decided to convert Z_1247kV to pu as shown below:
Z_base= (0.480^2)/(10^6)
Z_12.47kV ref to secondary= Z_12.47kV/ (12.47/0.480)^2=0.009 ohms
Z_12.47kV_pu= Z_12.47kV ref to secondary/Z_base=0.0433 pu
When i looked at the solution what i saw is that the pu value NCESS gets is 0.025 pu
Does anyone see where i went wrong with my pu conversion?