supra33202
Well-known member
- Joined
- Jan 6, 2012
- Messages
- 52
- Reaction score
- 1
I understand the MVA method, but I want to solve it with PU method.
Q3-54) Using the MVA method, find the 3-phase short-circuit fault current for ta transformer's secondary terminal. The low-side of the transformer is served by a generator. The generator's nameplate data indicates ratings of: 20 MVA, 23% reactance. The transformer's ratings are: 35 MVA, 13% impedance, 12.5/34.5 kV. Assume no short-circuit contributions downstream of the transformer.
The answer is D. 1,100 A, which I agree with MVA method.
My PU method:
Set Sb = 35 MVA, Vb = 34.5 kV
Iactual = Ibase * Ipu
Ibase = 35 MVA / [ sqrt(3) * 34.5 kV ] = 585.7 A
Ipu = Vpu / Zpu
Vpu = 34.5 kV / 34.5 kV = 1 pu
Zg, pu = 0.23 pu * (35 MVA/ 20 MVA) * (12.5 kV / 34.5 kV)^2 = 0.0528 pu (need to change the generator's bases from 20MVA to 35MVA and from 12.5 kV to 34.5 kV)
Zxfmr, pu = 0.13 pu
Since this is in series, Zpu = Zg, pu + Zxfmr, pu = 0.1828 pu
Ipu = 1 pu / 0.1828 pu = 5.47 pu
Iactual = 585.7 A * 5.47 pu = 3245 A ( which is not 1,100A)
What did I do wrong with my PU method?
Thanks!
Q3-54) Using the MVA method, find the 3-phase short-circuit fault current for ta transformer's secondary terminal. The low-side of the transformer is served by a generator. The generator's nameplate data indicates ratings of: 20 MVA, 23% reactance. The transformer's ratings are: 35 MVA, 13% impedance, 12.5/34.5 kV. Assume no short-circuit contributions downstream of the transformer.
The answer is D. 1,100 A, which I agree with MVA method.
My PU method:
Set Sb = 35 MVA, Vb = 34.5 kV
Iactual = Ibase * Ipu
Ibase = 35 MVA / [ sqrt(3) * 34.5 kV ] = 585.7 A
Ipu = Vpu / Zpu
Vpu = 34.5 kV / 34.5 kV = 1 pu
Zg, pu = 0.23 pu * (35 MVA/ 20 MVA) * (12.5 kV / 34.5 kV)^2 = 0.0528 pu (need to change the generator's bases from 20MVA to 35MVA and from 12.5 kV to 34.5 kV)
Zxfmr, pu = 0.13 pu
Since this is in series, Zpu = Zg, pu + Zxfmr, pu = 0.1828 pu
Ipu = 1 pu / 0.1828 pu = 5.47 pu
Iactual = 585.7 A * 5.47 pu = 3245 A ( which is not 1,100A)
What did I do wrong with my PU method?
Thanks!