A simple single phase power line with a motor question

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

sbsklewis

Member
Joined
Oct 12, 2012
Messages
9
Reaction score
0
For some reason I am not getting the answer.

A single phase power line with a purely resistive impedance of 200 ohms per conductor delivers power to an induction motor that requires 800 watts input power. Determine the generator power delivered to the line and motor combination, assuming a line current of 5 amperes.

I get 5800 watts, but the answer is 10800 watts.

 
Why are you multiplying 2? I never seen that...I though the line loses are: I^2*R, but don't get the other 2.

 
^Since it's a single phase load, current will be flowing in both conductors.

 
For some reason I am not getting the answer.

A single phase power line with a purely resistive impedance of 200 ohms per conductor delivers power to an induction motor that requires 800 watts input power. Determine the generator power delivered to the line and motor combination, assuming a line current of 5 amperes.

I get 5800 watts, but the answer is 10800 watts.
NASIR,

Each conductor (both coming and going) has the 200 ohm impedance. Effectively the power dissipated is:

P= (5^2)200 + 800W + (5^2)200

or

P = (5^2)(200*2) + 800W

 
Back