Is there specific situation when m*cp*del T is not advised when solving problems? I did a few problems and gotte them wrong when I used this formula, especially when dealing with air.
Any input will be appreciated.
If you use the “wrong” value of c
p you’re going to get it “wrong”. You can always get accurate results with c
p*[SIZE=11.0pt]Δ[/SIZE]T if you use the “right” c
p.
For example, if you have air going from 800°F to 810°F, but you use the value of c
p at 70°F you will be “wrong” i.e., off by a few percent. So, even here when there is small [SIZE=11.0pt]Δ[/SIZE]T (and c
p in that range is pretty darn constant) you will be wrong for using the wrong value.
Note: For 800°F to 810°F, c
p=0.257 Btu/lbm/F while for 70F c
p=0.24 Btu/lbm/°F -- a difference of about 7%
Another example; If you have air going from 70°F to say, 1000°F and use c
p evaluated at 70°F (or at 1000°F) your results will be less accurate than if you use c
p evaluated at the average temperature of roughly 540°F, which is 0.249 Btu/lbm/F (or if you use the average of the c
p values evaluated at 70°F and at 1000°F)
Some problems, however, explicitly ask you to use the “cold-air standard”. What specific problem did you get wrong by assuming constant c
p? I’m curious now.