I've found that sometimes the 30 degree XFMR phase shift is used, and sometimes it's seemingly irrelevant or disregarded. This is even the case when we aren't necessarily going through a transformer, but even when simply converting from a phase to a line voltage, for example -- this is perplexing. I don't have any specific examples at the moment, but if someone has a general explanation of when the phase shift must be used in PE-exam-relevant calculations, I'd be very grateful.
Good Question!
If we are only worried about magnitudes in the answer, then a lot of times the phase angles and the 30° phase shifts are ignored.
Example: If a question is asking to solve for apparent power in VA, but not complex power, then most of the time phase angles are ignored in calculations because they represent reactive power components. If you are not sure, you can always include phase angles in your calculations then only use the magnitude for the answer.
Now for the 30° phase shifts:
For a wye system, the line to line voltage
will always lead the respective line to neutral voltage by 30° if the system is positive sequenced and balanced.
For a delta system, the line current
will always lag the respective phase current by 30° if the system is positive sequenced and balanced.
Almost every system will be positive sequence and balanced unless the problem states otherwise.
If the system is
negative sequence (ACB or BCA) then instead of leading, they will lag, and vice versa. That is because the vectors now rotate in opposite directions about the origin.
If the system is
not balanced then the phase shift will be something other than 30°, and could very well be different for each of the three phases (i.e. each of the three phase shifts will not be the same).
It helps to have a look at the phasor diagrams:
For a wye system:
For a Delta System: