If either of these values are zero, what does that mean?
This is not always the case, just FYI. Especially for some older 3-phase plant/facility distribution systems.The neutral and ground are connected together at the main bonding jumper.
Depending where you measured itThis is not always the case, just FYI. Especially for some older 3-phase plant/facility distribution systems.The neutral and ground are connected together at the main bonding jumper.
- At service equipment, the voltage difference between the neutral conductor and the service equipment case will be 0 volts.
- At panelboards, the voltage difference between the neutral conductor and the equipment grounding conductor (panelboard case) will be equal to the voltage drop of the feeder neutral conductor, which is 3 volts.
- At branch circuits, the voltage difference between the neutral conductor and the equipment ground (ground contacts of the receptacle) will be equal to the voltage drop of the feeder and branch circuit neutral conductors, which is 4.5 volts (3 volts feeder and 1.5 volts branch circuit).
This is not always the case, just FYI. Especially for some older 3-phase plant/facility distribution systems.The neutral and ground are connected together at the main bonding jumper.