Nicely done. Quality should be about 0.179.I come up with (B)
I solved for the downstream quality and the computed the specific volume, using the quality. Then used v2/a2 = 4 * v1/a1 and solved for a2. Then computed diameter from a2. I came up with diameter d2 = 3.85 in.
10-4.On a side note: NEVER use a solenoid as an expansion device. You will wire draw the valve.
How did you come up with v2/a2 = 4v1/a1?I come up with (B)
I solved for the downstream quality and the computed the specific volume, using the quality. Then used v2/a2 = 4 * v1/a1 and solved for a2. Then computed diameter from a2. I came up with diameter d2 = 3.85 in.
On a side note: NEVER use a solenoid as an expansion device. You will wire draw the valve.
Conservation of mass flow and velocity constraint. m1=m2, rho1 A1 V1= rho2 A2 V2 and V2 = 4*V1... Combine and simplify. V= velocity v=specific volume= 1/rhoHow did you come up with v2/a2 = 4v1/a1?
Oh yes same, did not notice the small v being specific volume.Conservation of mass flow and velocity constraint. m1=m2, rho1 A1 V1= rho2 A2 V2 and V2 = 4*V1... Combine and simplify. V= velocity v=specific volume= 1/rho