Schaum's Electric Power System-per unit problem 2.11

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

electric

Active member
Joined
Mar 9, 2010
Messages
27
Reaction score
1
Location
KY
Can someone please help me to understand this problem;

"3 Phase, Y, 6.25KVA, 220V syn. Gen. has reactance of 8.4 ohms/ph. Using rated KVA and voltage as base values, determine per-unit reactance.

I am coming up with 1.08 pu and the solution is 0.627 pu.

Base Voltage=220/Sq Root 3 =127V

Base Current=[6250/3]/127=16.4A

Base reactance=127/16.4=7.744 Ohms

PU reactance = 8.4/7.744 = 1.08pu

Where is the error?

 
^I think the error is theirs.

I get: ZBase = (VLL-Base)2/SBase = 220V2/6250 VA = 7.744 Ohm

Zpu = 8.4/7.744 = 1.08

Their answer appears to be 1.08/sqrt3 = 0.626, which is not correct for the problem described.

 
^I think the error is theirs.
Their answer appears to be 1.08/sqrt3 = 0.626, which is not correct for the problem described.
Thanks Flyer_PE.

That's what I though too, but just didn't wanted to jump to the conclusion.

 
Back
Top