PU method and MVA method should yield same result?
Please look at the question
A 3-phase fault occurs at a location 1. This point is located downstream from a transformer and
a conductor. The conductor (3-ph/480V) has an impedance of Z = 2.0 ohms/phase and the
transformer has the following properties. 3-phase, 60 Hz, 13.2kV/480V, 10 MVA transformer
with Z = 8%. What is the short circuit current at the fault given only the information above?
Please look at the question