I want to get some opinions on this because I'm confused. Here is the situation:
550 HP motor at 480v, using 650FLC for calculations
Feeder breaker is 100% rated 800A CB
motor feeder cable is rated for 90deg C
Feeder breaker and motor terminations rated at 75deg C
Customer spec is use 35deg C for ambient temp correction
Neglecting voltage drop (distance unknown at this point) and assuming only 3 conductors
What size wire is needed for feeding the motor?
First, by NEC 430.22 we need 125% of motor FLC for the conductor which is 650*1.25=812a uncorrected cable minimum
With our cable at 90deg C, a 500MCM cable is good for 430a. Now correcting for 35deg ambient, 430*.96=412a per cable rating.
So using the corrected cable ampacity of 412a, a paralled run of 500mcm is enough ampacity to carry the 812a required.
Now the limiting factor of the terminations only being rated for 75deg C is where I am getting confused.
The site engineer who is a PE is saying we can use the 500mcm cables because even though we have to use the 380a rating of 75deg rated cable, the 125% of NEC 430.22 doesnt apply at 75dg since he already accounted for it in the sizing at 90deg values which doesnt make any sense to me.
I think we need to use parallel 600mcm in order to achive the min uncorrected ampacity requirement of 812 amps. NEC 110.14© allows for 90deg C to be used for correction but also states it cannot exceed the rating of the lowest rated termination. To me this means that 500mcm is good for 760a only, regardless of cable type used.
Sorry for the long post, any help/clarity is appreciated.
550 HP motor at 480v, using 650FLC for calculations
Feeder breaker is 100% rated 800A CB
motor feeder cable is rated for 90deg C
Feeder breaker and motor terminations rated at 75deg C
Customer spec is use 35deg C for ambient temp correction
Neglecting voltage drop (distance unknown at this point) and assuming only 3 conductors
What size wire is needed for feeding the motor?
First, by NEC 430.22 we need 125% of motor FLC for the conductor which is 650*1.25=812a uncorrected cable minimum
With our cable at 90deg C, a 500MCM cable is good for 430a. Now correcting for 35deg ambient, 430*.96=412a per cable rating.
So using the corrected cable ampacity of 412a, a paralled run of 500mcm is enough ampacity to carry the 812a required.
Now the limiting factor of the terminations only being rated for 75deg C is where I am getting confused.
The site engineer who is a PE is saying we can use the 500mcm cables because even though we have to use the 380a rating of 75deg rated cable, the 125% of NEC 430.22 doesnt apply at 75dg since he already accounted for it in the sizing at 90deg values which doesnt make any sense to me.
I think we need to use parallel 600mcm in order to achive the min uncorrected ampacity requirement of 812 amps. NEC 110.14© allows for 90deg C to be used for correction but also states it cannot exceed the rating of the lowest rated termination. To me this means that 500mcm is good for 760a only, regardless of cable type used.
Sorry for the long post, any help/clarity is appreciated.