A Power Plant uses a turbine driven synchronous generato rated 3-Phase, 150MVA, 13.8KV, 0.85 Lagging PF.
At rated conditions the Real Power output (MW) is most nearly:.......
I calculated as follows:
150MVA * 0.85PF * 1.73(for 3-Phase system) = 220 MW
However the book seems to answer the problem as if it was a single phase system as follows:
150MVA * 0.85PF = 127.5 MW
Now hear is my question why not multiply by Sqrt 3? By using the Sqrt 3 am I calculating Apparent Power instead of real power?