Hi @BebeshKing, the problem is essentially asking for the amount of fault power that originates from the generator that makes it through the transformer all the way to the fault bus. Transformers are known as "current limiting devices" because during fault conditions there is only so much current (or fault power) that they will "let through" to the other side, even if the transformer is being fed from an infinite bus.On problem 540, is it supposed to be just the MVA fault contribution of the generator G1 alone the one being asked? And should be just 834/0.23 =3626MVA? Or am I missing something? Could someone please explain?
thank you for your help!
Thank you @Zach Stone, P.E.. Now it's clear.Hi @BebeshKing, the problem is essentially asking for the amount of fault power that originates from the generator that makes it through the transformer all the way to the fault bus. Transformers are known as "current limiting devices" because during fault conditions there is only so much current (or fault power) that they will "let through" to the other side, even if the transformer is being fed from an infinite bus.
Because the transformer is in series with the generator, you'll have to take both into consideration when solving this question.
quick question for this guys, what if the problem ask for the short circuit MVA contribution of transformer T1,? will it be just 933/0.15= 6220MVA?On problem 540, is it supposed to be just the MVA fault contribution of the generator G1 alone the one being asked? And should be just 834/0.23 =3626MVA? Or am I missing something? Could someone please explain?
thank you for your help!
View attachment 16159
View attachment 16160
Wondering this myself. I think you are correct but am responding to bump this for others' input.quick question for this guys, what if the problem ask for the short circuit MVA contribution of transformer T1,? will it be just 933/0.15= 6220MVA?