Am having issues with the correct method of calculating Q freezing for this question. 

image.png

The solution in the book calculated  Q (freezing) = 10,000lb (.73) (144 Btu/lb)

image.png

I used cp of 72.63% water content pork should from ASHRAE Refrigeration book, which was 104 Btu/lb.(2006  R-9.5)

and got Q freezing to be 1,040,000Btu. 

My solution was 619,300 Btu/h, which is different than their solution of 624,900 Btu/hr.

So what is the correct method for such a problem?

Thanks in advance.

 
I used cp of 72.63% water 
I think you mean q_latent or h_fg... not cp. Correct?

Anyway, if you calculate q_latent per unit mass as w% x 144 Btu/lbm for w=0.7263 you get 104.6 Btu/lbm. So, its the same thing and the difference is a rounding error between using 73% or 72.63%

The difference between 619,300 Btu/h, and 624,900 Btu/hr is less than 1%

 