Find the Voltage regulation of a 25 kilovolt ampere, 480 V, 3 phase wye connected synchronous generator with the power factor of a) 0.81 lagging and b) 0.81 leading at rated voltage full load the winding resistance is 0.15 Ω per face, and the synchronous reactance is 6.1 Ω per face.
Why did they not use the 30 degree phase shift when converting from line to line to line to neutral? 480/1.733 = 277 angle -30 instead of 277 angle 0. Even assuming it was 0 why did they not keep the angles in VR formula. If they had I got 0.44 not 0.49. Using 30 degree phase shif I get 0.52. Why did they not keep angles in formula and why did they not use 30 degree phase shift? Ir appears they are working with phasors so I dont understand.
Why did they not use the 30 degree phase shift when converting from line to line to line to neutral? 480/1.733 = 277 angle -30 instead of 277 angle 0. Even assuming it was 0 why did they not keep the angles in VR formula. If they had I got 0.44 not 0.49. Using 30 degree phase shif I get 0.52. Why did they not keep angles in formula and why did they not use 30 degree phase shift? Ir appears they are working with phasors so I dont understand.