A section of a wye-connected 3-phase transmission line has a phase voltage rating of 15kV and a power rating of 30kVA. The per-phase line impedance is 75 ohm. What is the per-unit impedance?
solution: Zbase=(15k)^2/30kVA
Does the question imply that 30kVA is the phase load or you just always don't need to divide it by 3 to get the phase value? The way I read this question is 30kVA load is the 3-phase load.
solution: Zbase=(15k)^2/30kVA
Does the question imply that 30kVA is the phase load or you just always don't need to divide it by 3 to get the phase value? The way I read this question is 30kVA load is the 3-phase load.