Cram Volume 1- Question#48

Help Support Engineer Boards:

Joined
Dec 21, 2019
Messages
16
Reaction score
1
Hello everyone..

The subject question is related to over excited generator. The answer in the book is (B). 

But I when I tried to answer this question, my choice was (C) because it is over excited generator which means induced voltage is higher than terminal voltage. My understanding under this case the power factor for this system is lagging and I got more confident when I saw the the phasor diagram for synchronous generator supplying a lagging power factor in the NCEES reference book page#51. Therefore, I chose (C) because in lagging power factor VARs will be absorbed from the system and when the system is leading it means VARs will be supplied to the system, is it correct? 

Appreciate your help to clarify this question...

WhatsApp Image 2020-11-20 at 10.43.20 PM.jpeg

 

jd5191

Member
Joined
Nov 1, 2020
Messages
60
Reaction score
13
When you have lagging power factor, the generator is sending VARs to the grid.

Here's an example:

Suppose you're at 1pu Voltage and 1pu Current in a lagging system, say by 30 degrees

that means V = 1pu and I = 1pu -30°

Now what are VARs?

VARS = VIsin([SIZE=11pt]θ) = VIsin(θv - θi) = 1*1sin(0- (-30)) = 1sin(30) = 0.5pu[/SIZE]

[SIZE=11pt]Now what if you were leading by 30[/SIZE]°?

[SIZE=11pt]then VARS = VIsin(θv - θi) = 1*1sin(0-30) = -0.5pu[/SIZE]

You may also just want to memorize that from a generator's perspective, lagging means supplying VARs and leading means absorbing VARs with the math above as a sanity check.

 
Last edited by a moderator:

jd5191

Member
Joined
Nov 1, 2020
Messages
60
Reaction score
13
This isn't part of most study material, but you may be familiar with a generator capability curve below that shows positive Q (VARs) and relates it to lagging (with a typo) and Overexcited.



 

akyip

Member
Joined
Feb 7, 2020
Messages
298
Reaction score
93
Any synchronous machine (synchronous generator or synchronous motor) that is overexcited will always deliver reactive power.

 

akyip

Member
Joined
Feb 7, 2020
Messages
298
Reaction score
93
One thing I should note.

When a synchronous generator is over-excited, it has a lagging power factor.

When a synchronous motor is over-excited, it has a leading power factor.

But either way, when a synchronous generator or synchronous motor is over-excited, it delivers reactive power (Q, vars).

Synch Gen.png

Synch Motor.png

 

akyip

Member
Joined
Feb 7, 2020
Messages
298
Reaction score
93
Also a few phasor diagrams I drew out (not the most artistic) to try to explain over-excited synchronous machines.

I learned these from the Engineering Pro Guides book.

Basically, just remember:

  • Any synchronous machine (synch gen or synch motor) that is over-excited always delivers reactive power (Q, vars).
  • Overexcitation occurs when the real component of internal induced voltage Ea is greater than the magnitude of terminal voltage Vt: Re(Ea) > |Vt|
Overexcited synch gen phasor.png

Overexcited synch motor phasor.png

 
Joined
Dec 21, 2019
Messages
16
Reaction score
1
Thank you all for explanation and clarification, but why synchronous motor delivers reactive power while in equation (shown above) it is in negative which means in my understanding (when Q or P negative) it is absorbing instead of supplying power? 

 

akyip

Member
Joined
Feb 7, 2020
Messages
298
Reaction score
93
Thank you all for explanation and clarification, but why synchronous motor delivers reactive power while in equation (shown above) it is in negative which means in my understanding (when Q or P negative) it is absorbing instead of supplying power? 
The synchronous motor is a load. This is shown by the current I entering the positive terminal of the load. And when a load's reactive power value is negative, that means the load is delivering reactive power.

When a source's reactive power Q value is negative, the source is absorbing reactive power.

But when a load's reactive power Q value is negative, the load is delivering reactive power.

 
Last edited by a moderator:
Joined
Dec 21, 2019
Messages
16
Reaction score
1
The synchronous motor is a load. This is shown by the current I entering the positive terminal of the load. And when a load's reactive power value is negative, that means the load is delivering reactive power.

When a source's reactive power Q value is negative, the source is absorbing reactive power.

But when a load's reactive power Q value is negative, the load is delivering reactive power.
I got it.. thank you so much 

 