Two questions for some of you west coast guys who may be detailing concrete structures for seismic requirements:
Seismic Development: per ACI 21.7.5 bars should be developed in accordance with Equation 21-6 for a hooked condition and increased by 2.5 or 3.25 for a straight condition. I get this straight forward requirement, however in the example books I have this is nearly always ignored and the basic equations from ACI 12.2 are used...this includes splicing bars as well (Class B essentially)....am I missing a footnote or something else saying the seismic development can be waived for certain conditions? I can't find one example problem where 21-6 is used.
Resistance Factors (Phi): I understand the 0.6 factor from 9.3.4 should be used when shear capacity controls over flexural capacity (i.e. shear in a beam in special moment frame is based on flexural capacity of members so .75 can be used) and will normally control a shear wall (and doweling requirement at base). My question is in a intermediate or special moment frame would you ever use the 0.6 instead of 0.75 or 0.9? Seems like shear is always dependent on the nominal or probable flexural strength in these designs. I guess a shear wall could use a higher phi as well since flexure could control, although it is time consuming to calculate.
kevo? McEngr?
Seismic Development: per ACI 21.7.5 bars should be developed in accordance with Equation 21-6 for a hooked condition and increased by 2.5 or 3.25 for a straight condition. I get this straight forward requirement, however in the example books I have this is nearly always ignored and the basic equations from ACI 12.2 are used...this includes splicing bars as well (Class B essentially)....am I missing a footnote or something else saying the seismic development can be waived for certain conditions? I can't find one example problem where 21-6 is used.
Resistance Factors (Phi): I understand the 0.6 factor from 9.3.4 should be used when shear capacity controls over flexural capacity (i.e. shear in a beam in special moment frame is based on flexural capacity of members so .75 can be used) and will normally control a shear wall (and doweling requirement at base). My question is in a intermediate or special moment frame would you ever use the 0.6 instead of 0.75 or 0.9? Seems like shear is always dependent on the nominal or probable flexural strength in these designs. I guess a shear wall could use a higher phi as well since flexure could control, although it is time consuming to calculate.
kevo? McEngr?