Well-known member
Hi, I'm hoping this is a quick one to explain.
This problem has a 6.6kV utility service with source impedance of 0.94%. It is connected to a transformer serving a building at 480V. The transformer has 4.25% impedance and rated current of 1,720A. It asks for Isc at the transformer's secondary.
The problem solution simply takes:
Isc = FLA / Zeq
Zeq = 0.0094 + 0.0425= 0.0519 pu
FLA = given = 1720A
Isc = 33,141A
This is a fairly simple pu problem but I don't understand why you don't need to convert voltage bases for the utility source impedance. My solution was to find a new Zsource and then use FLA/ Zeq.
It seems like the utility voltage should matter in this sort of problem, but the solution doesn't include it at all. Can anyone explain why? Thanks for any last minute help!