E EEpowerOK Well-known member Joined May 23, 2013 Messages 107 Reaction score 4 Sep 20, 2013 #21 I have watched some on youtube. The piano sound was driving me crazy
Ship Wreck PE Well-known member Joined Aug 2, 2010 Messages 5,961 Reaction score 287 Location ga Sep 20, 2013 #22 EEpowerOK said: Thanks for clarifying. 3 phase delta or wye are both = sq rt 3 * V(line) * I (line) ? Click to expand... Yes to your question, but there are two ways to do them. On the Delta, Power (VA) = Voltage * Line current * sq rt 3 Also on the Delta, Power (VA) = Voltage * Phase current * 3 On the Wye, Power (VA) = Line Voltage * current * sq rt 3 Also on Wye, Power (VA) = Phase Voltage * Current * 3 This took me a while to get straight, but it makes since once you see the pattern along with the diagrams. And if you want to get more confused, throw in a neutral on the delta and get the high leg.
EEpowerOK said: Thanks for clarifying. 3 phase delta or wye are both = sq rt 3 * V(line) * I (line) ? Click to expand... Yes to your question, but there are two ways to do them. On the Delta, Power (VA) = Voltage * Line current * sq rt 3 Also on the Delta, Power (VA) = Voltage * Phase current * 3 On the Wye, Power (VA) = Line Voltage * current * sq rt 3 Also on Wye, Power (VA) = Phase Voltage * Current * 3 This took me a while to get straight, but it makes since once you see the pattern along with the diagrams. And if you want to get more confused, throw in a neutral on the delta and get the high leg.