Posted 13 October 2008 - 09:13 AM
This is probably going to sound like a really stupid question to power people, but I'm a computer engineer, so I don't know how to do it. I recently took some load readings off of some switchgear at a site I'm working on. I got the current draw on each phase, and the line-to-line voltages. I need to know the demand reading for the panel in both Amps and kVA. There is an example below:
Phase 1: 420A
Phase 2: 370A
Phase 3: 400A
L1-L2: 390V
L2-L3: 180V
L3-L1: 205V
Response to
wilheldp_PE
Unfortunately the electrical person(s) posting to this thread are making a wrong assumption: that the system is a 3ph 3w power supply, hence all the comments posted are incorrect. The system is a 200V/400V 1ph 3w system (some people refer to it as a 2ph 3w) with L3 being your neutral or "return". The instantaneous voltage would be only obtained if you measure all three phases at the same time, this will account for the variance when you add them, so when you add L2-L3 to L1-L3 (180+205=395V) it will equal approximately 390V. I forgot the power calculations but I am sure it can be easily found once since you now know the correct power supply configuration that you looking at. (I know the question may no longer be relevant but this is posted for the benefit of other people who may read this post. )