When you are given a piece of equipment and told its actual paramaters are those paramaters always taken as 1 per unit for the respective voltage, VA, and current?
For instance if we have a 10MVA generator, rated 13.8kV, 418A, is the rated voltage, current and VA equal to 1.0 where 1.0 pu corrosponds to the rated values listed above?
What about the rated impedance. Lets say we are told that X=15% then do we take rated impedance to be 1pu where 1pu equals 15% or do we take rated impedance to be .15pu?