NCEES Question #529

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

MDElec

Well-known member
Joined
Jun 9, 2008
Messages
54
Reaction score
0
On NCEES question #529, can anybody help me understand why the 480V is being divided by sqrt(3) in the solution? I understand they are subtracting the Voltage Drop from the panel voltage, but I can't figure out why the voltage is being divided by sqrt(3). I would really appreciate any help with this.

Thanks in advance!

 
The panel voltage is 480 V line-to-line. For the voltage drop calculation, you need the line-neutral voltage. (277 Volts for a 480 wye system)

VL-N=VL-L/sqrt(3)

 
The panel voltage is 480 V line-to-line. For the voltage drop calculation, you need the line-neutral voltage. (277 Volts for a 480 wye system)
VL-N=VL-L/sqrt(3)

Ok, dumbest question of the year...

277V - Line-to-Neutral Voltage

480V - Line-to-Line Voltage

831V - ?

831 = 480V * sqrt(3)

Thanks for the help by the way.

 
Back