Search results

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
  1. G

    Studying the NEC

    Be familiar on how to do voltage drop calcultions.
  2. G

    Thanks to Flyer PE & Dark Knight

    I finally passed the PE - power. Thanks to all on here. This was the most helpful resource i had. I also want to add a special thank you to Cableguy.
  3. G

    GEORGIA - RESULTS Oct 2010

    I finally passed the PE - power. Thanks to all on the EB.com especially to Cableguy.
  4. G

    NCEES 521

    Any better explanation, guidance to answering this question?
  5. G

    Power Depth Questions

    I don't believe so. You should take a look at the syllabus in the NCEES PE power sample question booklet. These topics are not included.
  6. G

    Kaplan afternoon problem # 37

    Boy oh boy am i lost.... How did u conclude the rotor is driven in the opposite direction? And since i did not grasp the concept yet, i don't know what will happen if it's a 6 pole machine.
  7. G

    Kaplan afternoon problem # 37

    A 3 ph, 4 pole synchronous motor and a 3 ph 4 pole slip ring induction motor are mechanically coupled. Their stators are also connected to a balanced 3 ph 60 hz supply. A 3 ph resistive load is connected across the slip rings. The frequency of the current in the resistive load is? a)30Hz b)60Hz...
  8. G

    Power Factor Correction Problem

    Thank you Dark knight!!
  9. G

    Power Factor Correction Problem

    Dark Knight, do u still have this question and solution available? I will like a copy. Thanks
  10. G

    Problems on NEC code

    Problem 18 Per 2008 NEC code section 430.32(1), for motors with service factor 1.15 or greater 1.25 * 28 = 35A and not 1.4 * 28 = 39.2A as indicated. Problem 19 Per 2008 NEC code section 430.32(1) for motors with temp rise over 40 deg, all other motors 1.15 * 26 = 29.9 and not 1.3 *26 = 33.8
  11. G

    Problems on NEC code

    Be careful with this article, example 18 and 19 are also incorrect.
  12. G

    Problems on NEC code

    The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps. Does anyone think it's incorrect? I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps
  13. G

    Battery characteristics and ratings

    The linke below might be a starting point http://www.mpoweruk.com/performance.htm
  14. G

    Power Flow/ Load Flow

    Any suggestions where to find sample problems on this topic? Or anyone has some sample problems they could share? Thanks
  15. G

    Power factor calculation

    I hope it does not make it to the PE but best be prepared than sorry u didn't. I am still struggling to understand the algerbraic soloution. Can you clarify what u meant by {"This means at full load, you have a phasor magnitude of 92 amps, with a j28 reactive component, along with an 87.x...
  16. G

    Power factor calculation

    Ques: A 3 phase induction motor draws 28A at no load and 92A at full load. What is the power factor of the motor at half load?
  17. G

    Power System Problem - Schaun's outline

    Motor: P = 75hp x 0.746kW/hp / 0.905 = 61.82kW pf = acos(0.895) = 26.49º Q = P tan(angle) = 61.82kW tan(26.49º) = 30.81kVAR Okay not sure if this is an obvious answer or not Why did you use the input power for the motor and not the output power to calculate the sytem KW?
  18. G

    Transformer with two secondary windings

    Can someone share what the voltage relationship will be for an ideal transformer with two secondary windings and one primary windings. I know for current it is Np * Ip = (Ns1 * Is1) + (Ns2 * Is2) Thanks
  19. G

    Per Unit Impedance

    I see what you are saying. I was working some sample problems and i used the the grainger formula but my answers did not match any of the proposed answers. When i looked at the solution in the book, the answer used Zbase equal (Vbase, KV)^2/ (Sbase, KVA). Not sure why they did that. That's...
  20. G

    Per Unit Impedance

    Power system analysis by grainger provides the formula (1.55) P.U Impedance =[ (actual impedance, ohm) x (base KVA)] / [(base voltage, Kv)^2 * 1000] If you do a derivation for PU Impdance = Zactual/Zbase where Zbase = (Vbase, KV)^2/ (Sbase, KVA) you get thesame result as shown above without...
Back