I find it fairly difficult to solve the problems pertaining to NEC code. Can anyone suggest me a quick and easy material/book to get upto speed?

Thanks in Advance!

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?"

They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps

Be careful with this article, example 18 and 19 are also incorrect.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps

Be careful with this article, example 18 and 19 are also incorrect.
Is the methodology incorrect? On the utility side, I rarely use the NEC, so I am trying to learn/understand these problems.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps
Isn't the 30 amp limitation for 240.4D new for 2008, and this set of questions based on 2005? So my 'guess' would be for 2005, the answers are correct, but not for us using 2008.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps
I agree that it seems incorrect. However, I think the answer should be 30 amps because 240.4D states that the 30 amp limit is applied after correction factors are applied.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps

Be careful with this article, example 18 and 19 are also incorrect.
Is the methodology incorrect? On the utility side, I rarely use the NEC, so I am trying to learn/understand these problems.
I would also appreciate an explanation of what is wrong with examples 18 and 19.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps
I agree that it seems incorrect. However, I think the answer should be 30 amps because 240.4D states that the 30 amp limit is applied after correction factors are applied.
You are probably right. That 2005 version was the one I used in 2006.

 
All,

How different is NEC 2005 from NEC 2008? I got my hands on 2005 handbook and wondering if that will make any difference if I take that with me to the exam. All those NEC code experts please share your views.

 
^Just an opinion: All those little changes from 2005 to 2008 make great fodder for exam questions.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps

Be careful with this article, example 18 and 19 are also incorrect.
Is the methodology incorrect? On the utility side, I rarely use the NEC, so I am trying to learn/understand these problems.
I would also appreciate an explanation of what is wrong with examples 18 and 19.
Problem 18

Per 2008 NEC code section 430.32(1), for motors with service factor 1.15 or greater

1.25 * 28 = 35A and not 1.4 * 28 = 39.2A as indicated.

Problem 19

Per 2008 NEC code section 430.32(1) for motors with temp rise over 40 deg, all other motors

1.15 * 26 = 29.9 and not 1.3 *26 = 33.8

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps

Be careful with this article, example 18 and 19 are also incorrect.
Is the methodology incorrect? On the utility side, I rarely use the NEC, so I am trying to learn/understand these problems.
I would also appreciate an explanation of what is wrong with examples 18 and 19.
Problem 18

Per 2008 NEC code section 430.32(1), for motors with service factor 1.15 or greater

1.25 * 28 = 35A and not 1.4 * 28 = 39.2A as indicated.

Problem 19

Per 2008 NEC code section 430.32(1) for motors with temp rise over 40 deg, all other motors

1.15 * 26 = 29.9 and not 1.3 *26 = 33.8
The NEC does allow the 39.2 A and 33.8 A values, but only if 35 A and 29.9 A are not high enough to prevent the motor from tripping on start up. The problems didn't seem clear what it was asking, but I assumed they meant the 39.2 A and 33.8 A values because problems 16 and 17 already used 35 A and 29.9 A.

 
The example number 11 " What is the ampacity of a #10 ZW2 conductor in a raceway with 5 current carrying conductors?" They have an answer of 32 amps.

Does anyone think it's incorrect?

I got 30amps ( see table 310.16 and 240.4D) X 0.8 (see table 310.15.B.2.a) = 24amps
I agree that it seems incorrect. However, I think the answer should be 30 amps because 240.4D states that the 30 amp limit is applied after correction factors are applied.


Question # 11 states what is the ampacity of a # 10 ZW2 conductor with total 5 current carrying conductor in a raceway. Article 240.4D should be considered to find out the protection of conductor only and should not be considered for ampacity itself.

Answer 32 Amps seems to be correct for ampacity of the condutor.

 
I know there has been some discussion about the results not being accurate or something like that. But have received some e-mails asking for this material. So here is the link...

NEC Problems

The problems are in that link. Just in case, I worked the problem with the 2005 version of the NEC.

 
Sorry to quote myself but there have been more requests for these problems.

I know there has been some discussion about the results not being accurate or something like that. But have received some e-mails asking for this material. So here is the link...
NEC Problems

The problems are in that link. Just in case, I worked the problem with the 2005 version of the NEC.
 