Zone of protection

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

kduff70

Well-known member
Joined
Mar 31, 2014
Messages
141
Reaction score
11
Location
New Jersey
Hi I was working a practice problem from the engineer guide by Graffeo problem 35 and I don’t quiet understand how his answer for back up protection are cb 2,7,6. I understand how cb 7 and cb 6 can be back up but not cb 2 I would think cb 2 would trip also I have attached the problem if some would care to explain the steps to me I’m not all the way sure what I missing.



relay.pdf

 

Attachments

  • relay.pdf
    15.7 KB
Kduff,

I purchased the Graffeo book back in August 2014. He sent me an email with some corrections for the book back in October 2014. #35 is explained more in the file I have attached. Hope that helps explain why breakers 2, 7, 6 are the backup protection.

Updated errata Explanations and Errata 10-10 p.pdf

 

Attachments

  • Updated errata Explanations and Errata 10-10 p.pdf
    257.1 KB
[SIZE=10.5pt]Thank you, I think I got now after looking a Graffeo study reference on protective relays The Art & Science of Protective Relayinghttp://www.gedigitalenergy.com/multilin/notes/artsci/artsci.pdf by C. Russell Mason on page 5 . He explain the field of protection for each breaker and where a fault will cause CB to open. So if look at the problem CB 4 zone of protection covers CB5 which is the line protection and it cover CB3 which is bus protection .Since CB7 and CB6 out of the zone protection they are the back up as well a CB2 I think that what he was saying . Your thoughts?[/SIZE]

 
Yes I agree, CB3 would be considered primary protection because it's on the same bus. CB5 would also be considered primary protection because it's on the same line. So CB2,CB6 and CB7 would all be considered backup protection.

 
Last edited by a moderator:
Yes I agree, CB3 would be considered primary protection because it's on the same bus. CB5 would also be considered primary protection because it's on the same line. So CB2,CB6 and CB7 would all be considered backup protection.
This...

 