Hey guys,
Typically when you are asked to calculate for the max power that can be sent on a transmission line given Vs, Vr, and theta, this should really be the 3-phase power, right?
The reason I ask is that in Shorebrook PE Power Exam question 30, the solution only uses the 1-phase power.
Generally speaking, in a transmission line, max power should really be the 3-phase power, correct? So: Pmax, line 3-ph = 3 * (Vs * Vr / X) * sin(theta)
Whenever I am asked to calculate the max power possible sent in synchronous generators, it usually refers to the 3-phase max power. So I would think the same concept applies to transmission lines...
Thanks for any input on this!