I feel like I might be missing something fundamental.
Take a look at this problem:
http://www.spinupexams.com/pgm-download_media.php?name=Week_2_QFTW_Question_Solution_Rev2.pdf
The ratio provided is 10:1 yet it is delta to wye. Is the ratio that is provided not the turns ratio? If it where the turns ratio wouldn't the Line to Neutral voltage be 460 and the Line to Line be 460*sqrt(3)
A similar example would be example 118 of the NCEES practice exam. It is a one line diagram with a Delta-Wye Transformer. Transformer is listed as 132-13.2. The answer for this one involves transforming the current across the transformer and is just a straight 10:1.
What am I missing?
Thanks
WEEK_2_QFTW_QUESTION_SOLUTION_REV2 (2).PDF
Take a look at this problem:
http://www.spinupexams.com/pgm-download_media.php?name=Week_2_QFTW_Question_Solution_Rev2.pdf
The ratio provided is 10:1 yet it is delta to wye. Is the ratio that is provided not the turns ratio? If it where the turns ratio wouldn't the Line to Neutral voltage be 460 and the Line to Line be 460*sqrt(3)
A similar example would be example 118 of the NCEES practice exam. It is a one line diagram with a Delta-Wye Transformer. Transformer is listed as 132-13.2. The answer for this one involves transforming the current across the transformer and is just a straight 10:1.
What am I missing?
Thanks
WEEK_2_QFTW_QUESTION_SOLUTION_REV2 (2).PDF