Transformer Ratings

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Fault current PU value will remain same but if I multiply PU value with the base current value (I_base=MVA rating/(1.732xV)) for amperage value the result will be different depending on the MVA rating being used .So in this situation should I use OA rating ?

By true rating I meant rating that can be used to find missing values i.e current on primary or secondary side of transformer.
 
I might be wrong here but i think fault MVA and transformer MVA are two separate things when it comes to fault calculation. Fault MVA determines fault current, same fault current will flow through the transformer.
 
Back
Top