Alright folks, I've been causing myself some brain damage on this problem..
Consider a single phase transformers rated 500 kVA, 33 - 2.4 kV, with internal impedance Z=+j1.0 ohms (low side).
If (3) of the above transformers are connected in a 3-phase transformer bank, wye on the high side and delta on the low side, what is the transformer bank rating?
I came up with the Bank rating of 57.2Y - 2.4Delta kV, 1.5MVA
My problems is trying to come up with the X rating.... I'm getting 0.33333 on the low side (Delta), but this conflicts with the solution of 0.086.
Is this solution wrong or in pu unit, or am I hurting my brain for no reason?
Thanks