Problem :
A 3 phase Delta-Y connected 15 MVA, 33/11 KV transformer is protected by CTs. determine CT ratio for differential protection such that circulating current ( through transformer delta ) does not exceed 5 A.
Solution Provided : I_delta=262.44 A
I_Y= 787.30A
If CT on high voltage side are connected in Y then CT ratio on high voltage side is 787.30/5
CT ratio on low voltage side is 262.44x5/sqrt(3).
If transformer is Delta-Y , do we always connect CTs in Y-Delta ?????
How they come up with CT ratio.
Can somebody explain ???????????