I would approach this analytically:
-you know it can't be 0 (that is the grounded phase)
-you know since you have some pos/neg Z it can't be 100
That leaves 114 and 173. If you understand the fault scenarios you know the phase V will rise 173 if no pos/neg Z
If we assume no pos/neg:
If = 0.577/0.1 = 5.77, so N rise is 0.577, add that vectorially to the phase and ph-g is now 1.73 x ph, but it affects both un- faulted phases equally, so no change in ph-ph V.
I would pick 114, but confirm it with algebra.
If = V(sum of seq Z) = 5 V = 5 pu
each ph contributes 1/3 (Z2) of If of opposite seq
Vdrop = 1.667 x 0.05 = 0.0833, rise in this case
0.0833 + ph V 0.577 = 0.66
0.66 x sqrt 3 = 1.144
114 kV