Although assigning the terms primary and secondary is somewhat arbitrary, the convention is that the system side of the CT is referred to as the primary and the relay/meter side of the CT is the secondary.

 
Although assigning the terms primary and secondary is somewhat arbitrary, the convention is that the system side of the CT is referred to as the primary and the relay/meter side of the CT is the secondary.
Thanks for the reply.

If the transducer is on the secondary, doesn't that make the turns ratio 5:400 (Np:Ns) ?

 
Don't confuse going across a power transformer (example, 138kV primary -> 69kV secondary) with going across a Current Transformer (primary->secondary).

When talking about a CT, you talk about "400 amps primary current" yields "5 amps secondary current". This gives you a CT Ratio of 400:5. The CT can be attached to a breaker (that does not have a "primary" and "secondary" side), or it can be attached to a power transformer (say a 138kV/69kV, that does have a "secondary" side). But don't let them confuse you with the term "secondary" - they can word the question very confusingly (and I bet they will ;) ). Just remember, the secondary side of a CT is the "low current" side, typically 5 amps.

 