Can anyone explain to me the question 61? not quite understand the solution. Another quick question. the exam book from NCEES only has 80 questions, but when I search in the Engineer Boards, I saw a lot more. is there another exam study book has more questions?
 

Attachments

  • IMG_4058.jpg
    IMG_4058.jpg
    43.7 KB
The key word in this problem is "instantaneously". Instantaneous basically means no time delay, or zero time delay.
Thanks. is there a table for relay setting option explain? I am just curious what are other settings for.
 
The instantaneous overcurrent trip function typically operates with a time setting (or cycle setting) of zero. In other words, the current is so great, that the relay should trip the OCPD immediately without a time delay.
 
The instantaneous overcurrent trip function typically operates with a time setting (or cycle setting) of zero. In other words, the current is so great, that the relay should trip the OCPD immediately without a time delay.
Are there any examples or articles that discuss how you would solve for the number of cycles if the trip function wasn't instantaneous?
 
Are there any examples or articles that discuss how you would solve for the number of cycles if the trip function wasn't instantaneous?

Sure.

If you are referring to time delay overcurrent protection (ANSI #51) as opposed to instantaneous overcurrent protection (ANSI #50), the TCC (time-current curve) for the relay or overcurrent protection device will tell you how much time typically in seconds (as opposed to cycles) that the device will take to begin operating to clear a fault.

Here is a video I published not too long ago on the subject with examples of the TCCs graphs:

 
Sure.

If you are referring to time delay overcurrent protection (ANSI #51) as opposed to instantaneous overcurrent protection (ANSI #50), the TCC (time-current curve) for the relay or overcurrent protection device will tell you how much time typically in seconds (as opposed to cycles) that the device will take to begin operating to clear a fault.

Here is a video I published not too long ago on the subject with examples of the TCCs graphs:


Thank you very much!
 