All Gurus,
CI: 2#51
3 phase transformer is provided with following information: 12MVA, 240/120kV, 4.6%Z
What is the new %Z at SB=50MVA and VB=230kV?
While calculating the new %Z, how do I know which voltage (120kV or 240kV) to use?
CI: 3#54
A 20MVA generator with 23% reactance has 12.5kV terminal voltage. This voltage is stepped up by a 35MVA transformer (13%Z) to 34.5kV. What is the fault current at the high voltage side of the transformer?
I used SB=35MVA and VB=34.5kV.
And generator per unit reactance would be Zg, new = 0.23 x (35/20) x (12.5 /34.5)2
Zpu, new = Zpu old x (SB new/SB old) x (VB old /VB new)2
But while analyzing the answer, the book does not use the voltage ratio - (12.5 /34.5)2 to get the answer.
Am I doing something wrong?
Thanks for your input.