What is the maximum rating of the Inverse Time Breaker to be used for the short-
circuit and ground fault protection of a branch circuit supplying a 3-phase, 50 hp, 460 V
wound rotor induction motor?
A. 90 A
B. 100 A
C. 150 A
D. 175 A
Considering 65A based on Table 430.250, I selected option A as the answer based Table 430.52 - Maximum Rating or setting of branch circuit short circuit and ground fault protective devices for wound rotor - Inverse time breaker. (65 * 1.5) = 97.5 A.
Unfortunately, as per the solution index, its the wrong answer. If it says maximum setting, then going by the rule, we cannot go beyond 150 % of the FLC.
Can someone please help interpret the table.
Thanks in advance.