Can someone please show the solution?
G1 has no load frequency of 61.5hz and a slope of 1MW/Hz. G2 has no load frequency of 61hz and a slope of 1MW/Hz
The two generators are supplying a real load totalling 2.5 MW at 0.8pf lagging.
a) at what frequency is system operating and how much power is supplied by each of the two generators
here's how i tried to solve it. If speed of one increases, speed of the other machine should decrease
gen 1 droop =(61.5-n)/61.5
gen 2droop =(61-n)/60.
the generator ratings are not given so how would you calculate the load shared by each generator
b)load is increased by 1 MW, what is new system frequency and how much power is supplied by each generator
c) with system configuration in part b, what will be the system frequency and generator powers be if governor set points of G2 are increased by 0.5 hz
I would appreciate any response.