I can come up with the 480v Base Isc of 1203A. However, I do not understand how they are obtaining the p.u. Isc? 1MVA is given, transformer has a 4% impedence, I assume that is the .04. But where are they getting the .025?
thanks,
thanks,
Since you are given the fault capability of the system in MVA the impedance is 1p.u. on a 40 MVA base. The value needed is the utility impedance on the transformer base (1MVA).
Zpu-tx = Zpu-utility*MVAtx/MVAutility
Zpu-tx = 1*1MVA/40MVA = 0.025
Iscpu = Vpu/(Ztx-pu+Zutility) = 1/(.04+.025) = 15.4 pu