That is a good question.Hi,
I understand the phase rotation doesn't make a difference with the solution, but why is the voltage on Phase B 120 degrees and not -120 degrees. Isn't the normal phase rotation ABC e.g. 0, -120, 120?
Thanks,
Kevin
No. The value 200+j100 is apparent power in kVA, not ohms. It's just odd seeing it represented in rectangular format rather than polar.Also, isn't the solution shown in the back IA = ZA / VA ?
After actually reading the question from the book i can understand now your question, to calculate for the line current,Actually, the right phase sequence for positive sequence is a-b-c rotated counterclockwise.. Some books have it the other way around..
After actually reading the question from the book i can understand now your question, to calculate for the line current,Actually, the right phase sequence for positive sequence is a-b-c rotated counterclockwise.. Some books have it the other way around..
I line = S*/V* where * is the conjugate of the phasor
Just like for calculating for power S= V x I* (single-phase)
Yes. VA is equivalent to apparent power (S) which is determined by the equation S=VI*.Should I always assume complex load if I see KVA for both single and 3 phase. And make sure I use the complex conjugate for current?