Hello,
I came across this question on the NEC practice exam :
A 3 phase 3 wire ungrounded 13.2 kV (phase to phase) wye connected source is connected to a balanced delta load that is grounded on CORNER A. The voltage measured between corner B and the ground is most nearly :
The answer is 13.2 kV.
Can someone please elaborate on this answer and if there is any good material I can refer to on this topic. Also how would the values change when the source is grounded ?
Thank you!
I came across this question on the NEC practice exam :
A 3 phase 3 wire ungrounded 13.2 kV (phase to phase) wye connected source is connected to a balanced delta load that is grounded on CORNER A. The voltage measured between corner B and the ground is most nearly :
The answer is 13.2 kV.
Can someone please elaborate on this answer and if there is any good material I can refer to on this topic. Also how would the values change when the source is grounded ?
Thank you!