M majorever Member Joined Dec 5, 2015 Messages 20 Reaction score 0 Sep 28, 2016 #1 I am confused about NEC Table 9 values. Why do we pick bottom values...............? what is the top row values in table 9 ? Please can someone help me out.?
I am confused about NEC Table 9 values. Why do we pick bottom values...............? what is the top row values in table 9 ? Please can someone help me out.?
cupojoe PE PMP Well-known member Joined Apr 9, 2013 Messages 519 Reaction score 136 Sep 28, 2016 #2 Top row is Ohms to Neutral per kilometer, bottom row is ohms to neutral per 1000 feet. See the top row in the table, it is a little weird how it is listed.
Top row is Ohms to Neutral per kilometer, bottom row is ohms to neutral per 1000 feet. See the top row in the table, it is a little weird how it is listed.
TWJ PE Well-known member Joined May 1, 2014 Messages 1,543 Reaction score 190 Location Texas Oct 10, 2016 #3 More than likely the problem will be worded for you to use the bottom row; however, CAUTION... this is a spot where they could try to trip you up.
More than likely the problem will be worded for you to use the bottom row; however, CAUTION... this is a spot where they could try to trip you up.
M majorever Member Joined Dec 5, 2015 Messages 20 Reaction score 0 Oct 11, 2016 #4 oh.........Thank you sooooooooooo..much It was bothering me. Finally got the answer ...............