So if third harmonics phase rms current would have been 7A instead of 3A (as given in the question) , then what would have been the Neutral third harmonics RMS current ?When you do the time domain math on a 3 phase system, you find that the triplen harmonics (primarily 180 hz but it occurs at higher multiples of 3) actually add on the neutral rather than cancel one another out.
Isn't it neutral current should be zero? Because for a balanced 3 phase 4 wire system there is no current flow through the neutral.
Please comment.
Triplen harmonics are additive in the neutral, even for balanced currents.Isn't it neutral current should be zero? Because for a balanced 3 phase 4 wire system there is no current flow through the neutral.
Please comment.
Only the triplen harmonics, which are odd multiples of 3.Thank you so much. Is it true about the 5th harmonic too ?
Same problem: balanced system with 5th harmonic currents. What will be the neutral current?