The problem states:
An electric generation facility uses a turbine-driven synchronous generator rated 3PH, 150MVA, 13.8-kV.
Per-unit reactances are: X"d=0.15; X'd=0.25; Xd=Xq=1.20
Assume terminal voltage (Et)=1.0 pu.
For a transient stability study at rated MVA, rated voltage, and unity power factor, the internal voltage (pu) and reactance (pu) for the generator should be, respectively:
A) 1.01 and 0.15
B) 1.01 and 0.25
C) 1.03 and 0.25
D) 1.10 and 0.25
I know the per-unit reactance for the generator should be 0.25, because we're told that we're doing a "transient stability study," but I'm having a hard time with the internal voltage part. The solution manual says I should be using (1.0+j0) pu for my current in the calculation of E'0, but doesn't elaborate any further, nor is it obvious to me why I would.
Does it have anything to do with the fact that I'm not given information about the circuit the generator is connected to, and therefore can't calculate the load current, and so must assume the base current is the same as the short-circuit current of the generator? This is the only thing I can think of, but I'm confident in this assessment.
Any help or insight would be very much appreciated.
Thanks.
An electric generation facility uses a turbine-driven synchronous generator rated 3PH, 150MVA, 13.8-kV.
Per-unit reactances are: X"d=0.15; X'd=0.25; Xd=Xq=1.20
Assume terminal voltage (Et)=1.0 pu.
For a transient stability study at rated MVA, rated voltage, and unity power factor, the internal voltage (pu) and reactance (pu) for the generator should be, respectively:
A) 1.01 and 0.15
B) 1.01 and 0.25
C) 1.03 and 0.25
D) 1.10 and 0.25
I know the per-unit reactance for the generator should be 0.25, because we're told that we're doing a "transient stability study," but I'm having a hard time with the internal voltage part. The solution manual says I should be using (1.0+j0) pu for my current in the calculation of E'0, but doesn't elaborate any further, nor is it obvious to me why I would.
Does it have anything to do with the fact that I'm not given information about the circuit the generator is connected to, and therefore can't calculate the load current, and so must assume the base current is the same as the short-circuit current of the generator? This is the only thing I can think of, but I'm confident in this assessment.
Any help or insight would be very much appreciated.
Thanks.