NCEES exam problem 129. I am now freaking out about voltage drop

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Sparky Bill PE

Senior, Master, Professional, Licensed Electrical
Joined
Jun 30, 2019
Messages
303
Reaction score
149
Location
Chattanooga TN
It says "You can use the other formula and get same answer, and I'm not getting same answer. I'm getting like 473.8 (of course just enough to make you chose wrong answer). What am I missing here? 

I don't see anywhere in reference handbook, or NEC telling me to use this method of keeping the resistance/reactance or converting to impedance. If I can use this formula, then why would we ever convert to effective Z?

Really gonna suck when this problem is on exam and its a coin flip on which formula to use to get the problem correct. 

image.pngimage.png

 
The one in the Reference manual just looks like an approximation. I'm getting the same as you, and i don't know what's wrong, except that the reference manual says it's an approximation, and this solution is basically V=IR, but the R is the cable. Seems more intuitive.

 
The one in the Reference manual just looks like an approximation. I'm getting the same as you, and i don't know what's wrong, except that the reference manual says it's an approximation, and this solution is basically V=IR, but the R is the cable. Seems more intuitive.
I have a lot of experience with the FE, and a lot of it was more of "trying to figure out the cute ncees way" of solving things instead of actually solving it like an engineer. I'm hoping I'm wrong on this. Otherwise, I know I'm going to be super pissed as soon as I see a voltage drop question and try to mind read how they want it. 

 
From the alternate method, I am getting Vd of 5.2V. Now given Vline is 480 and the Vd is per phase, so converting it to Vphase, we get V=277.128.
Vphase - Vd= 277.128 - 5.2 = 271.92. Converting it back to line value, Vline=sq.rt 3 * 271.92 = 470.99

Let me know if there is something wrong with this method.

 
From the alternate method, I am getting Vd of 5.2V. Now given Vline is 480 and the Vd is per phase, so converting it to Vphase, we get V=277.128.
Vphase - Vd= 277.128 - 5.2 = 271.92. Converting it back to line value, Vline=sq.rt 3 * 271.92 = 470.99

Let me know if there is something wrong with this method.
What is "alternate method"? Is that you calculating Z effective, then multiply that by current? Or is that you NOT finding Z effective and just using resistance/reactance? 

 
Alternate method being the alternate solution they mentioned above. I calculated the Zeff based on the formula on NEC chapter 9 Table 9. Then multiplied it by the current. The same formula is also given in the handbook.

NEC - 
image.png
 

Handbook - 
image.png

 
Alternate method being the alternate solution they mentioned above. I calculated the Zeff based on the formula on NEC chapter 9 Table 9. Then multiplied it by the current. The same formula is also given in the handbook.

NEC - 
View attachment 19686
 

Handbook - 
View attachment 19687
I didn't get 471, I'll post my work tomorrow and we can compare to what I'm doing wrong getting a different answer. 

 
This is from my notes when I solved it in the exam. Its a bit messy so let me know if you cant read it and I will try to write it up on a clean sheet.

example1.jpg

 
In my opinion, the angle is already taken care of when using the Zeff formula. We can either use the pf in Zeff calculation and mulitply with I mag OR use (R+jX) and then use I at an angle. 

 
In my opinion, the angle is already taken care of when using the Zeff formula. We can either use the pf in Zeff calculation and mulitply with I mag OR use (R+jX) and then use I at an angle. 
I agree angle in Z eff is taken care of, in your math there you have I * Z = 5.2. You're not using the angle of your current. Am I not supposed to be using the angle of my current provided by the power factor? My calculation is 400 at the angle of -36.9. 

 
I agree angle in Z eff is taken care of, in your math there you have I * Z = 5.2. You're not using the angle of your current. Am I not supposed to be using the angle of my current provided by the power factor? My calculation is 400 at the angle of -36.9. 
 You don't need to use the angle for your calcs. If you have NEC Handbook I highly recommend looking at the examples in chapter 9, right after table 9.

 
Yes that is correct. As far as I understand, when we use the Zeff formula, Zeff is already at the pf angle, -36.86. If we again multiply it by [email protected] degrees, the Vd will be at an angle of - 72.73 which will be incorrect. 

May be my understanding is incorrect, but that's how I thought it works.

 
 You don't need to use the angle for your calcs. If you have NEC Handbook I highly recommend looking at the examples in chapter 9, right after table 9.
Maybe that's what I'm doing wrong, so when doing voltage drop and using Z eff  you always take the current magnitude, not the complex current?

 
Maybe that's what I'm doing wrong, so when doing voltage drop and using Z eff  you always take the current magnitude, not the complex current?
That is correct, magnitude only because voltage drop of a circuit is in direct proportion to the resistance of the conductor and the magnitude of the current

 
NEC - Table 9 - Note 2

Ze (for other than .85 PF) = R*PF+Xl*sin(cos^-1(PF))

R(1000ft)=.029

R(250ft)=.029*(250/1000) = .00725

X(1000ft)=.048

X(250ft)=.048*(250/1000)=.012

PF=.8

Ze = .00725*.8+.012*sin(cos^-1(.8))

Ze = .013

Vd = I*Ze = 400*.013 = 5.2V

V = Vs(L-N)-Vd

V=277-5.2 = 271.8

V(LL) = V(LN)*1.732

V(LL) = 271.8*1.732 = 470.77 ≈ 471V

 
The pf drop from 0.85 to 0.8 has little effect. Basically sqrt(ratio): if pf goes down, Z goes up (Vdrop goes up), and the inverse. From table Z = 0.057

Vdrop = 400 x Sqrt3 x 250/1000 x 0.057 = 9.87, net 470.13

adjust Z for pf ~ 0.057 x sqrt(0.85/0.8)

= 0.0588

Vdrop 10.18, net 469.82

470 either way

 
The pf drop from 0.85 to 0.8 has little effect. Basically sqrt(ratio): if pf goes down, Z goes up (Vdrop goes up), and the inverse. From table Z = 0.057

Vdrop = 400 x Sqrt3 x 250/1000 x 0.057 = 9.87, net 470.13

adjust Z for pf ~ 0.057 x sqrt(0.85/0.8)

= 0.0588

Vdrop 10.18, net 469.82

470 either way
Yeah i found out my problem is I was using the complex current instead of just using the magnitude of current. 

 