I apologize. On DK PE's quote of my previous message above I meant to say the MVA rating of the transformer.
DK PE, your example does make sense. Where I get confused on this question is that the MVA rating of the transformer is accounted for in the computation even though the question asked for the contribution from the generator.
I'm not sure if that is correct. Do I make any sense on what I stated above, or am I making up a bunch of gibberish?
Thanks!
DK PE, your example does make sense. Where I get confused on this question is that the MVA rating of the transformer is accounted for in the computation even though the question asked for the contribution from the generator.
I think if I understand this correctly; the transformer needs to be included in the computation because even though there is more available short circuit current upstream from the transformer, the amount of available short circuit current at the fault location will be limited by the amount of MVA and impedance the transformer can handle, since the short circuit current will have to go through the transformer in order to get to the fault location.Transformers are not contributors to short circuit current. The transformer impedance acts to reduce the available short circuit current at the low-side bus.
I'm not sure if that is correct. Do I make any sense on what I stated above, or am I making up a bunch of gibberish?
Thanks!